Larry Cohen wrote:
That setup seems very lopsided, to have everything BUT the rear AC on the same leg! We ran into an overload problem in the cold running 2 1500 watt heaters hooked up to a 50A service...one of the circuit breakers on the inverter would trip occasionally. It would be nice to steal some of that minimally used second leg juice for some recepticles...how easy is it to do that to prevent heater overload???? "Haywagon" wrote in message news:naJEf.4082$7d.683@trnddc05... You did mean converter didn't you. But actually it is the circuit breaker panel that is with the converter/charger, referred to as the power distribution panel (pdp). Here is what I did- your circuit breaker (cb) panel has several connections, one cb for each circuit. I have one 20amp cb labeled air conditioner (ac), you might have two, considering you are 50amp and might have two ac units. I installed a 20amp outlet adjacent to the pdp connected to the ac cb. this is reserved for plugging in my 1500watt heater. You could install two 20amp outlets connected to each ac cb knowing you would not use the heater at the same time as the ac. Modern day ac units do not normally use as much power so you would be able to plug a small power requirement item in at the same time as you ran the ac. But another thing to consider is a heat strip in the current ac unit, some units can accept a kit that has every thing you need. I do not know how well the strip heat would work on the ducted ac units. -- Bill P. just Dog & ME At this time in life all that remains is left overs, some can be cherished as good others bad, but the only definite is that they are all that remains, main course is over. |
#22
|
|||
|
|||
Electric outlets at campgrounds
My winter stuff is at www.wolfswords.com under the 50 amp and winter links.
Yeah, a properly wired 50 amp pole is wonderful when it's well below zero. As for it being lopsided, the whole electrical thing is make up of one kluge on top of another. Someone entering the hobby has to look at how RVs are wired and wonder what fool came up with it. Steve "Larry Cohen" wrote in message ... That setup seems very lopsided, to have everything BUT the rear AC on the same leg! We ran into an overload problem in the cold running 2 1500 watt heaters hooked up to a 50A service...one of the circuit breakers on the inverter would trip occasionally. It would be nice to steal some of that minimally used second leg juice for some recepticles...how easy is it to do that to prevent heater overload???? "Haywagon" wrote in message news:naJEf.4082$7d.683@trnddc05... 14-50R is the proper 50 amp receptacle for a campground and it, in fact, has 240 vac connected to it. The difference is that within most large coachs they wire two separate 120 vac circuits, one to each side, off of it. http://users3.ev1.net/~crossstitch/RVWiring/wiring.html provides a complete explaination. |
#23
|
|||
|
|||
Electric outlets at campgrounds
Or, do some serious research and reading and learn about how to do it right.
Being here shows you've the right tools. Then, if you still can't grasp what's going on, spend that settlement money on an electrician. IMHO, when working on 220 volt service, if you have to ask, you need |
#24
|
|||
|
|||
Electric outlets at campgrounds
William Boyd wrote:
Larry Cohen wrote: That setup seems very lopsided, to have everything BUT the rear AC on the same leg! We ran into an overload problem in the cold running 2 1500 watt heaters hooked up to a 50A service...one of the circuit breakers on the inverter would trip occasionally. It would be nice to steal some of that minimally used second leg juice for some recepticles...how easy is it to do that to prevent heater overload???? "Haywagon" wrote in message news:naJEf.4082$7d.683@trnddc05... You did mean converter didn't you. No! He didn't. Larry, don't listen to BoydBrainless. He'll get you killed. He doesn't even know the difference between a converter and an inverter, or that the converter wouldn't have any effect upon your AC circuits, other than the power it would draw. After he figures out that a converter doesn't have any AC circuit breakers to trip, he'll try to give you more stupid and dangerous advice. Stick around for a bit, and Bob Hatch will help you with your question. you can trust what he tells you. Lon |
#25
|
|||
|
|||
Electric outlets at campgrounds
Well....thanks for your answers and insight...Since I dont know diddly about
electricity, other than I DO NOT like being tickled by it, I will certainly NOT mess with it myself! I think the idea of tying into the underused side of the leg is a good way to run that extra heater...surely wont be using the ac then!! "Steve Wolf" wrote in message ... My winter stuff is at www.wolfswords.com under the 50 amp and winter links. Yeah, a properly wired 50 amp pole is wonderful when it's well below zero. As for it being lopsided, the whole electrical thing is make up of one kluge on top of another. Someone entering the hobby has to look at how RVs are wired and wonder what fool came up with it. Steve "Larry Cohen" wrote in message ... That setup seems very lopsided, to have everything BUT the rear AC on the same leg! We ran into an overload problem in the cold running 2 1500 watt heaters hooked up to a 50A service...one of the circuit breakers on the inverter would trip occasionally. It would be nice to steal some of that minimally used second leg juice for some recepticles...how easy is it to do that to prevent heater overload???? "Haywagon" wrote in message news:naJEf.4082$7d.683@trnddc05... 14-50R is the proper 50 amp receptacle for a campground and it, in fact, has 240 vac connected to it. The difference is that within most large coachs they wire two separate 120 vac circuits, one to each side, off of it. http://users3.ev1.net/~crossstitch/RVWiring/wiring.html provides a complete explaination. |
#26
|
|||
|
|||
Electric outlets at campgrounds
Lon VanOstran wrote:
William Boyd wrote: Larry Cohen wrote: That setup seems very lopsided, to have everything BUT the rear AC on the same leg! We ran into an overload problem in the cold running 2 1500 watt heaters hooked up to a 50A service...one of the circuit breakers on the inverter would trip occasionally. It would be nice to steal some of that minimally used second leg juice for some recepticles...how easy is it to do that to prevent heater overload???? "Haywagon" wrote in message news:naJEf.4082$7d.683@trnddc05... You did mean converter didn't you. No! He didn't. Larry, don't listen to BoydBrainless. He'll get you killed. He doesn't even know the difference between a converter and an inverter, or that the converter wouldn't have any effect upon your AC circuits, other than the power it would draw. After he figures out that a converter doesn't have any AC circuit breakers to trip, he'll try to give you more stupid and dangerous advice. Stick around for a bit, and Bob Hatch will help you with your question. you can trust what he tells you. Lon INVERTERS http://www.go-rv.com/coast/do/catalo...=7&pageNum=111 CONVERTERS and pdps http://www.go-rv.com/coast/do/catalo...=7&pageNum=102 This is directed to those that think LON knows what he is talking about. -- Bill P. just Dog & ME At this time in life all that remains is left overs, some can be cherished as good others bad, but the only definite is that they are all that remains, main course is over. |
#27
|
|||
|
|||
Electric outlets at campgrounds
"Larry Cohen" wrote:
That setup seems very lopsided, to have everything BUT the rear AC on the same leg! We ran into an overload problem in the cold running 2 1500 watt heaters hooked up to a 50A service...one of the circuit breakers on the inverter would trip occasionally. It would be nice to steal some of that minimally used second leg juice for some recepticles...how easy is it to do that to prevent heater overload???? It should be quite simple. Simply move some of the loads to breakers on the other electrical bus in the entrance (circuit breaker) panel. If you're not familiar with how an entrance panel is wired, then check the Google, the library, or books in places such as the Home Depot or Lowe's. Don't forget that an RV panel is *branch* panel, and so the neutral and the safety ground are *not* to be tied together there. -- D.J., N8DO; FMCA 147762 dj[underscore]osborn at yahoo dot com |
#28
|
|||
|
|||
Electric outlets at campgrounds
William Boyd wrote: Lon VanOstran wrote: William Boyd wrote: Larry Cohen wrote: That setup seems very lopsided, to have everything BUT the rear AC on the same leg! We ran into an overload problem in the cold running 2 1500 watt heaters hooked up to a 50A service...one of the circuit breakers on the inverter would trip occasionally. It would be nice to steal some of that minimally used second leg juice for some recepticles...how easy is it to do that to prevent heater overload???? "Haywagon" wrote in message news:naJEf.4082$7d.683@trnddc05... You did mean converter didn't you. No! He didn't. Larry, don't listen to BoydBrainless. He'll get you killed. He doesn't even know the difference between a converter and an inverter, or that the converter wouldn't have any effect upon your AC circuits, other than the power it would draw. After he figures out that a converter doesn't have any AC circuit breakers to trip, he'll try to give you more stupid and dangerous advice. Stick around for a bit, and Bob Hatch will help you with your question. you can trust what he tells you. Lon INVERTERS http://www.go-rv.com/coast/do/catalo...=7&pageNum=111 CONVERTERS and pdps http://www.go-rv.com/coast/do/catalo...=7&pageNum=102 This is directed to those that think LON knows what he is talking about. -- i am trying to figure this thread out and see how it relates to my boat. i have a generator on my engine and another one that runs by its self. i have inverter and converter and air conditioner. i do not have a heater problem because when i am out i am running the engine. but between all the info so far it looks like lon is just a trouble maker or just dont like the other people because as i see it he is the one wrong. or i dont understand what he has in mind maybe the bob hatch can shed a little light on it. i might go do a little goggling too. i posted this on the bottom to try and make heads and tails out of the thread. |
#29
|
|||
|
|||
Electric outlets at campgrounds
Larry Cohen wrote:
That setup seems very lopsided, to have everything BUT the rear AC on the same leg! We ran into an overload problem in the cold running 2 1500 watt heaters hooked up to a 50A service...one of the circuit breakers on the inverter would trip occasionally. It would be nice to steal some of that minimally used second leg juice for some recepticles...how easy is it to do that to prevent heater overload???? "Haywagon" wrote in message news:naJEf.4082$7d.683@trnddc05... 14-50R is the proper 50 amp receptacle for a campground and it, in fact, has 240 vac connected to it. The difference is that within most large coachs they wire two separate 120 vac circuits, one to each side, off of it. http://users3.ev1.net/~crossstitch/RVWiring/wiring.html provides a complete explaination. Just as a guess about the lopsided loading on the 50 amp systems. The neutral wire would be less likely to be overloaded. And then it could have something to do with 50amp to 30amp adapters, again I have never had a 50 amp system. Some one that has plugged in to a 30amp circuit using the adapter might be able to shed some light on it, I think one of their air conditioners might not run. Or things that is on the lesser loaded side might not be connected. -- Bill P. just Dog & ME At this time in life all that remains is left overs, some can be cherished as good others bad, but the only definite is that they are all that remains, main course is over. |
#30
|
|||
|
|||
Electric outlets at campgrounds
"Stan Birch" wrote in message
On Sat, 4 Feb 2006 "Bob Hatch" wrote: My guess is he's repeating things he's been told. by people that have less than full working knowledge of RV, and electrical systems. BTW, a couple of days ago a guy told me that Winnebago was discontinuing 30 amp service in all its motorhomes. Starting, I think he said, with the 2007 models, all would be 50 amp. That move would be counter to the general trend of the remainder of the industry which is no longer offering 50A service. Which ones are "no longer offering 50A service". Provide a couple of links please. I've looked at several so far and all offer 50A or have it as standard on larger rigs. With more efficient modern A/Cs, mere 30A service is more than adequate to address most RVing needs. But with Winnebago, you never know. They seem to be incorporating a whole lot of "$tandard" features which many of us consider somewhat useless. You mean "some of us". :-) -- "Twenty years from now, you will be more disappointed by the things you did not do, than the ones you did. So throw off the bowlines, sail away from the safe harbor and catch tradewinds in your sail." Mark Twain http://www.bobhatch.com http://www.tdsrvresort.com |
Thread Tools | |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
electric appliances | Anon | Europe | 9 | September 24th, 2005 02:33 PM |
Which factory outlets sell Burberry in Japan? | Dee | Asia | 1 | April 14th, 2004 05:04 PM |
electrical outlets in Europe hotel bathrooms | Jan Hanford | Europe | 85 | February 14th, 2004 02:55 AM |
Bahamas electric outlets | Pistolero1987 | Caribbean | 1 | February 11th, 2004 11:29 PM |
Campgrounds on mapping software | Steve B. | USA & Canada | 1 | January 10th, 2004 12:39 PM |